消防问答 > 消防给排水 提问

消防水泵试水管

1、当消防水泵设有流量测试装置时,可否不设DN65的试水管?

2、 每台消防水泵出水管上应设置DN65的试水管,并应采取排水措施。此处的排水措施是指什么?我记得好象是要间接排水?

请写下您的回答回答

הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


共 2 回答

消防网友73006 22-08-03

1.流量测试装置可以设置在DN65的试水管上
2.DN65试水管不需要间接排水,可以多台泵试水管可以合用一根排水总管回流到消防水池

0 0 [回复]举报

消防网友54901 22-08-03

1、流量测试装置的设置与试水管的设置没关系。流量测试装置的目的是检测流量。试水管的目的是检测水泵能否自动启动,以及水力警铃和压力开关能否动作。

2、试水管排水应该没有间接排水的要求。间接排水是防止排水管堵塞或其他排水污染消防用水,试水管上的阀门是常闭的,直接和排水管相连不会受到影响。

0 0 [回复]举报