消防问答 > 自喷灭火系统 提问

【问】水流指示器灵敏度高,末端放水不报警怎么处理?

各位麻烦帮忙分析下,水流指示器灵敏度高,放末端不报警怎么处理,末端压力0.2-0.4Mpa左右,七层楼。末端管路有点远,50米左右。


请写下您的回答回答

输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


共 3 回答

乌伤浪人 24-05-24

邪了,灵敏度高,末端放水又不报警?是怎么判断它灵敏度高的呢?
不能报警只能说明灵敏度有问题啊。如果高位水箱补水的水流方向没问题,那可能是桨片故障或微动开关故障。

1 0 [回复]举报

南明离火 24-05-24

输出报警信号时,流量应大于15.0 L/min且小于或等于37.5 L/min; 灵敏度 属于正常范围,估计水流坏了

0 0 [回复]举报

shawu 24-05-27

如果你说的末端压力是静压的情况下,末端放水时孔口的压力要减去总水损,这时候要看看动压多少,如果太低那么用公式Q=(10p)的0.5次方算出的孔口流量可能会处在调定的报警流量以下,从而导致水流指示器不报警

0 0 [回复]举报

最新问题

关闭

关闭