消防问答 > 自喷灭火系统 提问

自动喷水系统

我们单位没有设置高位消防水箱,设置了稳压装置,但稳压泵控制柜为手动启动方式,末端试水装置压力表为0.3兆帕以上,二个月前为0.35兆帕,现在为0.31兆帕。请问,这种状态正常吗?谢谢

请写下您的回答回答

输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


共 4 回答

陈泽平 24-10-06

改成自动状态

0 0 [回复]举报

张治福 24-10-08

稳压泵控制柜应处于自动方式,另压力波动属于正常现象,热胀冷缩原理

0 0 [回复]举报

阳明心 24-10-08

二个月降0.04Mpa,可以理解为正常状态,应继续观察,看后续下降情况再判断是否有较大的泄漏。 

0 0 [回复]举报

磊中 24-10-08

稳压泵应为自动状态,设稳压泵的目的就是为了有少许的压力降会补上,不过这里压降这么少是没什么问题的,稳压泵的启停也是设置一定压降的,

0 0 [回复]举报

最新问题

关闭

关闭