避难间可开启外窗的问题

这种只能在一面设置可开启外窗,这样设置可以吗?

请写下您的回答回答

输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


共 5 回答

周家斌 23-08-08

看设计时间是否执行新通规

0 0 [回复]举报

玺望成真   回复: 周家斌23-08-08

只有一面可以设置的怎么处理呢

0 0 [回复]举报

安洪全 23-08-08

只能一面开启外窗的话,就需要上机械防烟系统了。


建筑防烟排烟系统技术标准 GB51251-2017

3.3.12 设置机械加压送风系统的避难层(间),尚应在外墙设置可开启外窗,其有效面积不应小于该避难层(间)地面面积的1%。有效面积的计算应符合本标准第4.3.5条的规定。

0 0 [回复]举报

@mad 23-08-08

避难间一面开窗可以啊,《消防设施通用规范》第11.2.4条说了,而且《建筑防烟排烟系统技术标准》第3.2.3条被废除了的。

1 0 [回复]举报

周家斌   回复: @mad23-08-08

是的,通规有变化。

0 0 [回复]举报