消防问答 > 消防给排水 提问

一体式消防水泵房设置位置及是否有效

在建筑中部位置下挖设置消防水泵房,地面以上无建筑,机柜及水泵均在地下,一体式消防水泵房设置爬梯通向地面,地面仅有检修井盖,是否可行,有无规范支持。

请写下您的回答回答

输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


共 3 回答

安洪全 24-04-24

一体化预制泵站工程技术标准 CJJ/T285-2018

0 0 [回复]举报

消防网友68723 24-04-25

5.5.9 消防水泵房的设计应根据具体情况设计相应的采暖、通风和排水设施,并应符合下列规定:
    1 严寒、寒冷等冬季结冰地区采暖温度不应低于10℃,但当无人值守时不应低于5℃;
  

5.5.14 消防水泵房应采取防水淹没的技术措施。

0 0 [回复]举报

周家斌 24-04-28

这要看当地可有限制使用的规定。

0 0 [回复]举报

最新问题

关闭

关闭