消防问答 > 自喷灭火系统 提问

预作用喷淋系统可以联动启泵吗?

一消老师讲到预作用喷淋系统如果一个防火分区内2个烟感或1个烟感加1个手报报警,预作用喷淋泵需要启动,这样对吗?

请写下您的回答回答

输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


共 6 回答

LHH2737 24-06-27

不完全对,GB 50116-2013第4.2.2条预作用系统的联动控制设计,应符合下列规定:联动控制方式,应由同一报警区域内两只及以上独立的感烟火灾探测器或一只感烟火灾探测器与一只手动火灾报警按钮的报警信号,作为预作用阀组开启的联动触发信号。由消防联动控制器控制预作用阀组的开启,使系统转变为湿式系统;当系统设有快速排气装置时,应联动控制排气阀前的电动阀的开启。湿式系统的联动控制设计应符合本规范第4.2.1条的规定。

0 0 [回复]举报

玺望成真   回复: LHH273724-06-27

规范里没有要求烟感和手报能联动启泵,而且烟感手报可以联动水泵的话水泵误动作的概率太高了。

0 0 [回复]举报

最帅游客   回复: 玺望成真24-06-28

之前消火栓手动报警按钮还可以直接启泵呢,若有烟感和手报共同的反馈信号,说明已经着火了,还不起泵等啥呢

不过一般有人值班的场所主机都打的手动,即便收到信号也不会起泵。

0 0 [回复]举报

李海波   回复: 玺望成真24-06-28

你规范吃的不透,验收和设计规范还不一样。

0 0 [回复]举报

玺望成真   回复: 最帅游客24-06-30

说的是预作用喷淋系统。

0 0 [回复]举报

玺望成真   回复: 李海波24-06-30

规范有相关要求吗?具体哪个规范哪条受累告知一下。

0 0 [回复]举报

最新问题

关闭

关闭