电气火灾监控系统控制器能否安装在变电所内?

问:电气火灾监控系统控制器能否安装在变电所内?


根据民用建筑电气设计标准 GB51348-2019,控制器应安装在建筑物的消防控制室内。


13.5.9 电气火灾监控系统的控制器应安装在建筑物的消防控制室内,宜由消防控制室统一管理。


条文说明:

13.5.9 关于电气火灾监控系统控制器的安装,国内有两种观点:一是将其安装于消防控制室,二是将其安装于变电所。安装在消防控制室的理由是该系统也是火灾报警系统,且消防控制室在24h内均有人值班,便于维护和管理。安装于变电所内的理由是该系统监测的是配电线路的接地故障,一旦出现问题值班人员可以马上处理。

    从上述看二者都有道理,但从工程实际情况看,很多变电所无人值班或非24h值班。因此,本标准规定将其安装于消防控制室。