【常见问题】室外消火栓栓口设置不合理,地下式消火栓未设标识

【问题描述】栓口设置不合理,地下式消火栓未设标识

 

《消防给水及消火栓系统技术规范》 GB50974-2014

7.2.2 市政消火栓宜采用直径DN150的室外消火栓,并应符合下列要求:

    1 室外地上式消火栓应有一个直径为150mm或100mm和两个直径为65mm的栓口;

    2 室外地下式消火栓应有直径为100mm和65mm的栓口各一个。

 

 

7.2.11 地下式市政消火栓应有明显的永久性标志。

来源:青岛市建设工程消防验收给排水专业常见问题(2024版)

请写下您的评论评论

הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


共 1 评论

张治福 24-11-11

这是没有设置65的接口的问题吗?

0 0 [回复]举报

更多资讯

关闭

关闭