对于层高高于6米的无吊顶走道排烟量,是按《烟规》高于6m的空间考虑排烟量,还是按60m³/(h·㎡)计算且不小于13000m³/h?对于面积小于100m2的有外窗房间和小于50m2的无外窗房间(走道机械排烟),净高高于6m时,是否需要考虑排烟?

对于层高高于6米的无吊顶走道排烟量,是按《烟规》高于6m的空间考虑排烟量,还是按60m³/(h·㎡)计算且不小于13000m³/h?对于面积小于100m2的有外窗房间和小于50m2的无外窗房间(走道机械排烟),净高高于6m时,是否需要考虑排烟?

请写下您的回答回答

הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


共 1 回答

潘天坤 24-11-22

一般来说,公共建筑的走道可不按大于6米的场所计算排烟量(地区技术文件有特别要求的除外),其他情况的走道如何执行可能有点争议

房间和走道均设置排烟设施时,走道排烟量按按60m³/(h·㎡)计算且不小于13000m³/h

仅走道设施排烟设施时,走道排烟量按照13000考虑即可,如果暗房间总建筑面积比较多可以适当考虑加一些暗房间的排烟量

一般建筑面积小于100平方米的有可开启外窗的房间和建筑面积小于50平方米的无窗房间是不需要考虑排烟设施,电影院除外

上述言论为根据国家规范的个人理解和交流探讨,不一定正确,也不能作为依据
有些地区技术文件可能有特别规定,建议楼主多与区域内设计、审查及验收等专家交流,具体以他们意见为准