消防问答 > 防烟排烟 提问

丁类厂房位于地上,面积没超5000㎡,但用于高温生产工艺,是否需要做排烟?

请教各位老师,若丁类厂房位于地上,面积没超5000㎡,但用于高温生产工艺,是否需要做排烟?

请写下您的回答回答

输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


共 3 回答

云中飞翔 24-12-02

这个规范上描述的不是太清楚,高温丁类厂房本身就会产生高温多烟,不管是否大于5000平米,都应该设置排烟设施。

0 0 [回复]举报

jinyanwu 24-12-03

“除”的意思就是例外,所以这个第三条就是例外,也就是不需要。

就是建筑面积大于5000㎡也不需要,更何况小于。

根据《建规》

可以看出来其实通规是进行了放宽,建规要求的是丁类大于5000就要设置排烟(不分是否高温工艺),通规大于5000需要排烟,但高温工艺除外。

0 0 [回复]举报

潘天坤 24-12-04

个人从规范文字理解,认为:高温生产工艺的丁类厂房不需要设置排烟设施,无关面积要求

规范正文未多做描述,条文说明和实施指南也没有看到相关解释,也没有听说编制组有宣贯明确,不知道后面会不会明确此内容

上述言论为根据国家规范的个人理解和交流探讨,不一定正确,也不能作为依据
有些地区技术文件可能有特别规定,建议楼主多与区域内设计、审查及验收等专家交流,具体以他们意见为准

0 0 [回复]举报

最新问题

关闭

关闭