消防安全泄压阀一直动作泄水,怎么调试



林宇111 | 2024-11-14 17:33
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 4

Dopp 2024-11-14 18:46 10 [回复]举报

一般顺时针旋转就行,但是要根据图纸设计确定到多少公斤泄压合适,需多试几遍

阿龙 2024-11-15 16:47 20 [回复]举报

先把泄压阀前端的阀门关掉(保险起见),再根据你的系统设计压力进行调紧泄压阀,顺时针是紧,逆时针是松,调一点点后锁紧泄压阀下方调节固定螺母,最后再打开阀门观察还漏不漏,还漏水的话重复上述操作,多试几次,不要一下子调太多,不然会把泄压值调的过高。

如果要调到系统设计压力的话就要启泵操作了,需要关闭系统的出水阀门,就在水泵房进行管网短循环测试,步骤还是跟上述一样,一般都是把泄压压力调到水泵设计工作压力值的1.1倍,需要一点点慢慢调试才能到想要的值。

消防资源网 2024-11-15 17:08 20 [回复]举报

AX742X安全泄压持压阀。用于给水,空调,消防管道系统。介质为水,温度≤80℃。用来稳定阀前管道压力,当阀前压力超压时,主阀开启排水,管道压力下降到设定值以下时,主阀关闭。可以通过导阀调节螺钉来设定压力值,设定值在一定范围内可调节。

AX742X安全泄压持压阀由双腔直流式主阀,导阀,针阀、球阀、和压力表等零件组成。


工作原理:首先要设定好主阀开启压力。松开导阀防松螺母,顺时针转动导阀螺钉,螺钉向下动作。调节弹簧被压缩,施加一定推力到导阀芯。这时主阀开启压力升高逆时针转动导阀调节螺钉,弹簧压力释放,作用在导阀芯上推力减少,这时主阀开启压力降低。通过压力表可以观察主阀前管道压力值。设定好后,拧紧防松螺母。

当阀前压力升高时,导阀膜片下腔压力也随之升高。超过设定值后,膜片带动导阀芯向上动作,导阀开启,主阀膜片上腔水排出。压力下降,主阀芯在膜片上下腔压力差作用下开启,主阀开始排水,管道压力开始下降。

导阀膜片下方压力也随之降低,当压力降低到设定值以下时。在调节弹簧作用下。导阀芯关闭。主阀膜片上腔压力逐渐升高,由于主阀膜片面积大于主阀芯面积,在二者压力差作用下。主阀芯关闭。主阀停止排水。

总结:
一.  设定开启压力时,应逐渐升高阀前压力。使其在设定值开启。并记录压力表数值,然后继续升高进口压力。使主阀保持全开启排放状态(即主阀排出流量不再增加)。记录主阀的排放压力。然后再逐渐降低进口压力,直至主阀关闭,记录阀门的回座压力
二.  重复调整两次以上,直到主阀开启压力,排放压力。回座压力都稳定为止。
三.  当需要手动泄压时。可以开启主阀盖上的泄压球阀,这时主阀膜片上腔压力下降。主阀随之开启泄压,泄压球阀出口应该接管到排水沟渠。
四.  主阀开启压力差,在P<0.5MPa时,偏差值±0.02MPa。P≥0.5MPa时,偏差值±0.04MPa。
五.  排放压力≤1.08P(P为开启压力值。)

幽暗岁月 2024-11-15 21:20 00 [回复]举报

检查泄水阀的供电是否正常,正常,检查管道是否漏水,泄压阀是否漏水。均正常调整自动泄压阀泄压自动控制器的泄压压力,对应高度。