消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

末端试水装置平时压力表静压

末端试水装置压力表平时静压多少正常?谢谢

阿进 | 2024-11-19 10:35
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 3

jinyanwu 2024-11-20 10:18 10 [回复]举报

静压其实没有什么作用,主要是动压是否合格;静压根据设置位置、水泵扬程不同是不一样的;

日常静压仅能判断管网有压力,但如管网、阀门等存在堵塞但不严重,静压有可能是符合要求的,但动压就不符合了;所以管网试压看的是动压;也就是试水情况下或者火灾情况下管网有水流动时的真实压力;


阿进   回复: jinyanwu2024-11-20 10:37

谢谢


0    0 [回复]举报

折耳根 2024-11-20 10:27 00 [回复]举报

自动喷水灭火系统等自动水灭火系统应根据喷头灭火需求压力确定,但最小不应小于0.10MPa


稳压泵的设计压力应保持系统最不利点处水灭火设施在准工作状态时的静水压力应大于0.15MPa

关闭

关闭

手机APP下载