消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

配电房门需要甲级门吗,

通用规范没有规定了?

消防网友67477 | 2024-11-30 13:29
请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


回答 | 4

懒得说 2024-11-30 14:41 00 [回复]举报

开向建筑内的门要甲级防火门;开向室外的门为乙级防火门

消防网友77957 2024-11-30 16:27 00 [回复]举报

应该需要,应该从严处理,且甲级门和乙级门价格费用差不多

jinyanwu 2024-12-02 09:47 00 [回复]举报

通规要求是防火门,但没有级别要求,这个是建规规定:

xie00 2024-12-02 11:23 00 [回复]举报

8.3.2 变电所防火门的级别应符合下列规定:
    1 变电所直接通向疏散走道(安全出口)的疏散门,以及变电所直接通向非变电所区域的门,应为甲级防火门;
    2 变电所直接通向室外的疏散门,应为不低于丙级的防火门

关闭

关闭

手机APP下载