办公与宾馆合建的建筑,设置喷淋问题

办公与宾馆合建的建筑,宾馆部分小于3000平,办公不设中央空调。总建筑面积超过3000平,是否设置自喷系统?

丽波 | 2024-12-05 21:39
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 6

一路同行 2024-12-06 08:21 00 [回复]举报

8.1.9 除建筑内的游泳池、浴池、溜冰场可不设置自动灭火系统外,下列民用建筑、场所和平时使用的人民防空工程应设置自动灭火系统:
    1 一类高层公共建筑及其地下、半地下室;
    2 二类高层公共建筑及其地下、半地下室中的公共活动用房、走道、办公室、旅馆的客房、可燃物品库房;
    3 建筑高度大于100m的住宅建筑;
    4 特等和甲等剧场,座位数大于1500个的乙等剧场,座位数大于2000个的会堂或礼堂,座位数大于3000个的体育馆,座位数大于5000个的体育场的室内人员休息室与器材间等;
    5 任一层建筑面积大于1500㎡或总建筑面积大于3000㎡的单、多层展览建筑、商店建筑、餐饮建筑和旅馆建筑;

单层是否大于1500平方




丽波   回复: 一路同行2024-12-06 09:16

单层均小于1500平

0    0 [回复]举报

丽波   回复: 丽波2024-12-06 10:12

一栋多层公建,办公与宾馆合建,办公不设中央空调,总建筑面积超过3000平,每一层均小于1500平,宾馆部分是小于3000平,工程定性是公寓式宾馆,要按照总建筑面积看,超过3000平设自动灭火系统。

0    0 [回复]举报

jinyanwu 2024-12-06 09:16 00 [回复]举报

个人意见,仅供参考:

可以同时参考一下建规和通规有关规定。

首先确定一下建筑一些属性:是否属于一类高层?二类高层?多层建筑?任一层面积?总面积?

另外可以设置的应该是自动灭火系统,不仅仅可以设置自喷。建规上建议采用自喷。

张治福 2024-12-06 10:07 00 [回复]举报

1、建筑定性:该建筑如果以宾馆为主,就定性为旅馆建筑。

2、面积按整栋建筑的面积计入(包含宾馆和办公区域)。

3、再对照标准是否需要设置。


PS:你这栋建筑以宾馆使用性质为主,定性为旅馆建筑;总建面超3000,根据要求,需要配置自动喷水灭火系统

李勤 2024-12-06 10:59 00 [回复]举报

两个业态在同一个建筑,之间是否做到完全独立分隔(防火墙、疏散、排烟等),没做到就不能独立看待,指示按综合路看整体建筑。