消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

丙类仓库内设置厨房的规定

电子产品仓库内设置厨房的规定查了一下规范不知道是否到位,想请教一下:建筑设计防火规范 GB50016-2014(2018年版)3.3.9办公室、休息室严禁设置在甲、乙类仓库内,也不应贴邻。
6.2.3 建筑内的下列部位应采用耐火极限不低于2.00h的防火隔墙与其他部位分隔,墙上的门、窗应采用乙级防火门、窗,确有困难时,可采用防火卷帘,但应符合本规范第6.5.3条的规定:5 除居住建筑中套内的厨房外,宿舍、公寓建筑中的公共厨房和其他建筑内的厨房

如果从上述规定来看,丙类仓库设置厨房只要满足防火分隔要求应该是可以的。

法亦有道 | 2025-04-10 16:48
请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


回答 | 1

LHH2737 2025-04-10 17:00 30 [回复]举报

不可以

建筑防火通用规范4.2.7 仓库内不应设置员工宿舍及与库房运行、管理无直接关系的其他用房

关闭

关闭

手机APP下载