消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

戊类库房需要排烟吗?

刘老师,地下戊类库房都是不可燃物品,应该不需要做排烟吧?

shej | 2021-08-17 17:58
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 4

刘丽波 2021-08-17 21:40 00 [回复]举报

除长度超过40米的疏散走道,其余不需要考虑排烟设施。

shej   回复: 刘丽波2021-08-24 10:41

刘老师,不是超过20米的走道就要排烟吗?

另外再请教您一下,我这里有4个二三十平的丙类库房(食品库房),总共100平左右,地下一层,要做排烟吗?

0    0 [回复]举报

阳明心 2023-04-11 17:07 00 [回复]举报

应该是长度超过20米的走道,没有自然排烟条件的需要机械排烟。

阳明心 2023-04-11 17:13 00 [回复]举报

4 高度大于32m的高层厂房(仓库)内长度大于20m的疏散走道,其他厂房(仓库)内长度大于40m的疏散走道。


抱歉,更正一下,刘老师对的,是40米。


见建规8.5.2

关闭

关闭

手机APP下载