消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

湿式报警阀压力差

湿式报警阀系统测和供水侧压力表显示压力不一样,造成这样的原因有哪些?这种情况会导致什么后果?

奕扬 | 2021-09-09 11:16
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 2

小凡 2021-10-07 16:37 00 [回复]举报

正常情况下,系统侧压力值会高于供水侧,随着管网补压动作,系统侧压力值会继续身高,原则上系统侧压力值不大于系统的设计的工作压力值就行,超过了就需要通过末端排水卸掉一部分的压力,防止爆管了。


阳明心 2023-04-13 11:28 00 [回复]举报

系统侧压力一般略高于供水侧,如果高很多应该有其他原因。但不是补压的原因。因为补压是补到供水侧的,而不是补在系统侧。

关闭

关闭

手机APP下载