耐火等级一级建筑中走道两侧耐火极限不小于1.0的隔墙。

请问,1、在走道上设置固定观察窗是否需要采用A类防火玻璃。2、走道上设置玻璃隔墙需要采用A类防火玻璃且满足完整性及隔热性不小于1.0h,那为什么玻璃门在走道上却没有这样的要求。3、及走道上的门可以不采用耐火极限不小于1.0h的门,那么固定窗是不是同等道理。

WeiHL | 2021-11-21 13:55
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 1

消防小陈 2021-12-30 10:14 00 [回复]举报

防火玻璃的要求要满足隔墙规定的耐火极限,不一定都是1.0h。玻璃门是因为规范里有明确规定哪些场所使用哪种门,这个不用太纠结。固定窗使用,如果使用玻璃满足墙体耐火极限就可以,如果不满足就不能使用,或者使用了疏散距离就要从房间内算,而不是从疏散门计算。