防烟分区 清晰高度 自然排烟窗有效面积

老师,麻烦问下:防烟分区吊顶高度3米,挡烟垂壁高度600mm,清晰高度是2.4m还是1.5m呢?计算自然排烟窗有效排烟面积的底是2.4还是1.5呢?


l123 | 2022-01-19 16:19
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 3

学生 2022-01-20 11:18 00 [回复]举报

烟规4.6.9:走道、室内空间净高不大于3m的区域,其最小清晰高度不宜小于其净高的1/2,清晰高度应为1.5m。

挡烟垂壁高度600mm,则储烟仓为600mm,自然排烟窗有效排烟面积的底应为2.4m。

刘丽波 2022-01-20 12:38 00 [回复]举报

防烟分区净高3米,挡烟垂壁高度600mm,储烟仓为600mm,最小清晰高度为1.5米。有条件自然排烟窗按储烟仓范围内的计算,无法满足可以计算到1.5米标高处。

l123   回复: 刘丽波2022-01-21 11:51

好的,谢谢老师