请教关于33米高以下高层建筑封闭楼梯间靠外墙时是否需要设置固定窗的问题?

根据《烟规》 3.3.11 设置机械加压送风系统的封闭楼梯间、防烟楼梯间,尚应在其顶部设置不小于1m2的固定窗。靠外墙的防烟楼梯间,尚应在其外墙上每5层内设置总面积不小于2m2的固定窗。,对于这一条款,有一定疑问,想请教老师,盼回复。问题如下:

   (1)假如防烟楼梯间不靠外墙,意味着无法设置外窗,此种情况下,只需考虑防烟楼梯间正常机械正压送风即可是吗?

    (2)如果建筑是33米以下的高层建筑,设置封闭楼梯间,且楼梯间靠外墙,是机械正压送风,从建筑立面方案上考虑出发,尽量不在楼梯间外墙上开洞的情况下,是否需要在其外墙上每5层内设置总面积不小于2m2的固定窗?

     规范上说开固定窗是为了救援方便,而且只说了防烟楼梯间,对封闭楼梯间机械防烟的情况如何要求的哪?

wenhua | 2022-06-15 22:50
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0

回答 | 7

刘丽波 2022-06-16 07:29 00 [回复]举报

执行3.1.3-2后半句的情况需要设置固定窗 。

wenhua   回复: 刘丽波2022-06-16 10:40

收到刘老师的回复,谢谢!可是我没太搞懂您的回复,可能我的问题没表述清楚,我想问的情况是靠外墙的封闭楼梯间如果采用机械正压送风是否需要在其外墙上每5层内设置总面积不小于2m2的固定窗?这个情况,《烟规》 3.3.11条没有说,只说了靠外墙的防烟楼梯间,尚应在其外墙上每5层内设置总面积不小于2m2的固定窗。盼复,谢谢!

0    0 [回复]举报

刘丽波   回复: 刘丽波2022-06-16 13:03

不靠外墙只需要顶部的1平固定窗。

0    0 [回复]举报

wenhua   回复: 刘丽波2022-06-16 17:07

就是说靠外墙的封闭楼梯间如果采用机械正压送风只需顶层部位设置1平米的固定窗,无需每五层设置总面积不小于2平米的固定窗,是吧?谢谢!

0    0 [回复]举报

刘丽波   回复: wenhua2022-06-18 09:57

是不靠外墙的

0    0 [回复]举报

李哥抓   回复: 刘丽波2023-03-21 09:45

刘老师,他的意思是:靠外墙的封闭楼梯间(设置了机械加压送风),是不是可以不用5层内设置固定窗?因为规范只写了靠外墙的防烟楼梯间,没有说靠外墙的封闭楼梯间。

0    0 [回复]举报

刘丽波 2023-03-21 21:18 00 [回复]举报

目前阶段,不靠外墙的防烟楼梯间及靠外墙的封闭楼梯间设置机械加压时,均需在最顶部设1平方米的固定窗。6月1日以后按建筑防火通用规范2.2.4执行