大空间厂房的疏散指示标志

厂房内划定了人员行走的路线,两边设置了护栏,这种情况怎么布置疏散指示标志和应急照明呢。

珍珠baby | 2022-06-21 14:45
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 5

深圳消防 2022-06-28 17:08 10 [回复]举报

疏散指示牌可以吊装,应急照明也可以吊装。

珍珠baby   回复: 深圳消防2022-07-14 11:01

问题吊装没有位置啊,而且疏散指示标志不需要在一米以下吗

0    0 [回复]举报

周家斌 2022-06-28 22:03 00 [回复]举报

可以参照走道的设置方式设置,但是在行走路线外的大空间内也要按照相应路径设置。

珍珠baby   回复: 周家斌2022-07-14 11:00

是设置在护栏上吗,那样取电比较困难。可不可以在通道上粘贴蓄光型标志辅助呢,丁戊类厂房。

0    0 [回复]举报

永锅 2022-09-15 17:01 00 [回复]举报

大空间厂房的疏散指示标志的设置:

1)当疏散通道两侧设置了墙、柱等结构时,方向标志灯应设置在距地面高度1m以下的墙面、柱面上;当疏散通道两侧无墙、柱等结构时,方向标志灯应设置在疏散通道的上方。

2)方向标志灯的标志面与疏散方向垂直时,特大型或大型方向标志灯的设置间距不应大于30.,中型或小型方向标志灯的设置间距不应大于20.;方向标志灯的标志面与疏散方向平行时,特大型或大型方向标志灯的设置间距不应大于15m,中型或小型方向标志灯的设置间距不应大于10.。