消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

消防水鹤设计

遇到一个项目,要做市政消防水鹤,要求用自打井代替消防水源,1.请问消防水鹤的设计流量是多少?2.是否可用自打水井作为消防水源?3.自打水井需满足哪些要求(流量、水位,连续供水时长)?4.建设方需提供自打水井的哪些参数及报告文件?5.自打水井是否需要两个作为两路消防水源?6.自打水井对消防水鹤进行供水时水泵如何控制(是每次加水时人工手动开启水泵加水,还是通过何种方式能自动启泵加水)?7.供水泵采用何种形式(潜水泵还是正常泵房内设置的消防泵)?

fendou44 | 2022-06-22 17:21
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 6

刘丽波 2022-06-23 23:36 00 [回复]举报

自打井水需要2眼,保证枯水期有水的情况下可以不设消防水池,但一般都很难满足,所以需要设置消防水池。消防水泵采用轴流深井泵。

fendou44   回复: 刘丽波2022-06-24 09:04

老师设置消防水池的话需要保证多长时间的消防水量呢,也是两小时么(相关规范在哪里),消防水鹤的设计流量是30L/s么?

0    0 [回复]举报

刘丽波   回复: fendou442022-06-29 19:06

要考虑枯水期无水,需要设置全部所需消防水量。一个水鹤的水量是30l/s

0    0 [回复]举报

fendou44   回复: 刘丽波2022-07-28 15:22

老师,考虑枯水期无水的话设置消防水池,消防水池容积具体如何计算?如按时长一个水鹤30L/s,时长按多少计算?如不按时长计算,要如何计算?请明示,谢谢老师

0    0 [回复]举报

刘丽波   回复: fendou442022-07-30 14:48

按《消水规》3.6.1计算。本工程实际需要多少消防水量就选用多少。

2    0 [回复]举报

fendou44   回复: 刘丽波2022-08-03 10:27

明白,谢谢老师指导

0    0 [回复]举报

关闭

关闭

手机APP下载