消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

此种情况执行<<烟规>>哪一条条文呢?4.6.3-3款还是4.6.3-4款?

通廊式公建,走道两侧房间建筑面积部分大于100,部分小于100,且两侧房间均不满足自然排烟要求,请问走廊排烟执行<<烟规>>4.6.3-4款还是4.6.3—3款?为何?

wenhua | 2022-06-28 15:54
请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


回答 | 4

@mad 2022-06-28 17:44 10 [回复]举报

建议参考上海的地方规范第5.2.2.2注3,就很清晰了。



消防黄河 2022-06-28 23:09 00 [回复]举报

应采用4.6.3.4,规范说的很清,当房间设置时。另,您所描述情况应考虑大于一百平房间排烟问题,不能对外开窗自然排烟,就需设置机械排烟。

刘丽波 2022-06-29 12:34 00 [回复]举报

看走道周围房间是否设置排烟设施。全设执行4.6.3-4;部分设置执行4.6.3-3

充楞装傻 2022-07-05 16:08 00 [回复]举报

按4.

该走廊包含3和4的情况,4要求更高,取高。

关闭

关闭

手机APP下载