消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

求教:高层住宅(30层)相邻两家的入户门水平距离不足1米,符合《建筑设计防火规范》有关条文要求吗?

1、如图下图:高层住宅(30层)相邻两家的入户门YHM1水平距离不足1米,应该不符合《建筑设计防火规范》 GB50016-2014(2018年版) 5.5.2的 要求。这样理解对吗?

2、如图下图:根据《建筑设计防火规范》 GB50016-2014(2018年版) 5.5.32的要求,防火门YHM3是需要安装的,这样理解对吗?

szhdxz | 2022-07-20 10:34
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 4

周家斌 2022-07-20 12:02 10 [回复]举报

规范条文5.5.2说的不是这入户门,“避难间”的防火门既然图纸设计了,就要安装,但是可以变更取消。

szhdxz   回复: 周家斌2022-07-20 13:53

谢谢您,我明白了。是”宜“不是”应“!可以变更。

0    0 [回复]举报

消防黄河 2022-07-20 13:06 20 [回复]举报

1、所述理解不正确。该条款指同一空间向外的两个疏散门,与两户住宅入户门不同概念。2、审核时有,就应按设计安装。审核时无,也可不装。

szhdxz   回复: 消防黄河2022-07-20 13:49

谢谢您!明白了。

1    0 [回复]举报

关闭

关闭

手机APP下载