1.根据火灾自动报警设计规范,6.1.4 可设置无人值守的条件第一条:本区域内无需手动控制的消防联动设备(是否指的只有报警功能,无联动功能的区域机)。

2.火灾自动报警设计规范图集14X505-1 第44页图示,区域机可联动控制屋顶排烟风机(此处和图集第14页对区域机解释不匹配)。


| 2022-07-26 10:41
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 3

wsxiebo 2022-07-27 11:50 10 [回复]举报

我理解的是区域报警系统与区域火灾报警器是没有关联的,如上图所示,区域火灾报警控制器相当于口语化的报警分机

zjx   回复: wsxiebo2022-07-28 09:58

是的,区域火灾报警系统和区域报警控制器是不同的概念,后者可以具备联动功能。但是对于6.1.4的条文解释只有报警功能的区域控制器才可设置无人值守。

0    0 [回复]举报

wsxiebo   回复: zjx2022-07-28 16:08

条文说明不具备与规范正文同等的法律效力,仅供使用者作为理解和把握规范规定的参考。满足6.1.4条第二款的条件也可以

0    0 [回复]举报