消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

商业建筑中带消防码的筒灯是否能兼用日常和应急照明?有具体规范出处吗?

商业建筑中带消防码的筒灯,是否能兼用日常和应急照明?有具体规范出处吗?

抹灰工 | 2022-08-12 16:43
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 3

一成道人 2022-08-12 19:23 00 [回复]举报

GB51348-2019《民用建筑电气设计标准》

13.6.5 消防疏散照明灯及疏散指示标志灯设置应符合下列规定:    

1 消防应急(疏散)照明灯应设置在墙面或顶棚上,设置在顶棚上的疏散照明灯不应采用嵌入式安装方式。

充楞装傻 2022-08-13 11:39 00 [回复]举报

你这种灯不能实现集中控制,有消控室的不能用...

而且是220V供电吧~8米以下都不让用。。。


楼上的必要看~~以专业规范为准 

消防应急照明和疏散指示系统技术标准 GB51309-2018

4.5.3 灯具在顶棚、疏散走道或通道的上方安装时,应符合下列规定:
    1 照明灯可采用嵌顶、吸顶和吊装式安装。+


 4 设置在距地面8m及以下的灯具的电压等级及供电方式应符合下列规定:
      1)应选择A型灯具;

消防网友73006 2022-08-13 15:51 00 [回复]举报

一个是持续型,另外一个非持续型。建议分开设置,江苏这边公共建筑不允许合用

关闭

关闭

手机APP下载