防火分区的划分

防火构件可直接划分民用建筑的防火分区吗

其他行业 | 2022-09-07 07:08
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 2

林继青 2022-09-07 11:54 00 [回复]举报

一般采用防火墙,确有困难时也可以其它防火分隔措施

感恩 2022-09-14 10:07 00 [回复]举报

根据《建筑设计防火规范》GB50016-2014(2018年版)第5.3.3 条规定:防火分区之间应采用防火墙分隔,确有困难时,可采用防火卷帘等防火分隔设施分隔。采用防火卷帘分隔时,应符合本规范第6.5.3条的规定。防火分区之间可采防火墙、防火卷帘、来分隔,未提及防火构件,而建筑防火构造包括:钢梁柱包覆、内外墙体、吊顶、管道竖井、电缆桥架包覆、通风管道包覆等。根据以上来看,如果是墙体的防火构件,且耐火极限满足防火分区间的防火要求,是可以划分的,其他防火构件则不行。