消防水池容量含室内消火栓、自动喷淋系统,是否需要计算水炮的容量一起呢

消防水池容量含室内消火栓、自动喷淋系统,是否需要计算消防水炮的容量一起呢

殇~~ | 2022-10-12 13:41
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 4

周家斌 2022-10-12 14:14 00 [回复]举报

殇~~   回复: 周家斌2022-10-18 13:54

哪个规范第几条呢

0    0 [回复]举报

消防黄河 2022-10-13 08:07 10 [回复]举报

计算该防护区用水量时喷淋和水炮取较大值,再加室内栓的量。

永锅 2022-10-14 08:59 10 [回复]举报

自动跟踪定位射流灭火系统技术标准 GB51427-2021 >第4.5.2条、4.5.3条解释的很清楚。