消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

气体灭火系统防护区的围护结构可以采用防火卷帘吗?

保护区与比较大,分2个防护区,为了方便联通,分割墙部分采用防火卷帘,平常防火卷帘提升上去,发生火灾时下降到楼面。

这样就形成了2个独立的防护区,是否可行?

黄辉 | 2020-10-14 10:17
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 6

消防网友346 2020-12-03 17:19 40 [回复]举报

不可以的,因为除了防火分隔以外,防护区还要承受一定的压力,要满足承压能力不小于1200pa,防火卷帘达不到这个要求的。

黄辉   回复: 消防网友52182020-12-07 08:55

谢谢您的解答!

0    0 [回复]举报

贾工 2021-01-27 15:05 10 [回复]举报

不可以。在住建部给出的最新回答中:在防火卷帘能够达到墙体防火系数时,也不允许使用防火卷帘替代分隔墙。

黄辉   回复: 贾工2021-01-27 19:21

谢谢解惑!

0    0 [回复]举报

李勤 2021-03-18 10:50 30 [回复]举报

不可以,首先防护分隔需要承受压力,第二卷帘门下降速度和可靠性直接影响灭火药剂的灭火效果(全淹没)

黄辉   回复: 李勤2021-03-19 09:32

谢谢!

0    0 [回复]举报

关闭

关闭

手机APP下载