消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

格栅吊顶通透面积小于70%,采用下喷时,是否需要加设挡水板,有没有具体规范要求

格栅吊顶通透面积小于70%,采用下喷时,是否需要加设挡水板,有没有具体规范要求

消防砖家 | 2023-02-13 01:02
请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0

回答 | 8

秘密1 2023-02-13 11:17 00 [回复]举报

说些我的个人理解,不需要,《自动喷水灭火系统设计规范》7.1.10条规定,除这两条,其他场所或部位不应采用挡水板;而7.2.3条采用下喷是因为上喷头所流出的水会经过管道的阻碍,因此管道下方会增设喷头,采用挡水板是因为上喷头喷出的水会淋湿下喷头从而影响下喷头动作,所以在都是下喷头的情况下不需要采用挡水板进行保护。

永锅 2023-02-13 12:04 00 [回复]举报

根据《自动喷水灭火系统设计规范》要求:装设网格、栅板类通透性吊顶的场所,当通透面积占吊顶总面积的比例大于 70%时,喷头应设置在吊顶上方,并符合下列规定:(7.1.13)

1 通透性吊顶开口部位的净宽度不应小于 10mm,且开口部位的厚度不应大于开口的最小宽度;

2 喷头间距及溅水盘与吊顶上表面的距离应符合 7.1.13的规定。

一、依上述条文可知,以下两种情况,均需在吊顶上方和下方同时布置洒水喷头:

1、当通透面积占吊顶总面积的比例不大于70%时,吊顶上方和下方应同时设置洒水喷头。

2、当通透面积占吊顶总面积的比例大于70%,但不符合7.1.13的两个条件时,吊顶上方和下方应同时设置洒水喷头。

二、当吊顶上方和下方同时布置洒水喷头时,应注意以下要求:

1、装设网格、栅板类通透性吊顶的场所,系统的喷水强度应按《自动喷水灭火系统设计规范》表5.0.1、表5.0.4-1~表5.0.4-5规定值的1.3倍确定,且喷头布置应按本规范第7.1.13条的规定执行。(5.0.13)

2、报警阀组控制的洒水喷头数计算,仅需将数量较多一侧的洒水喷头计入报警阀组控制的洒水喷头总数。

3、关于系统的设计流量,吊顶的上方和下方应分别计算,以较大者为准。

4、安装在吊顶下方的洒水喷头,宜设置挡水板,为照顾美观,挡水板可设置在吊顶的内侧

秘密1   回复: 永锅2023-02-15 10:42

7.1.13条说的是应设置在,并没有说增设啊,你上下均设喷头的结论是如何得出的?

1    0 [回复]举报

张牙舞爪的张 2023-02-13 14:08 00 [回复]举报

徐海金 2023-02-13 15:34 00 [回复]举报

当然需要。你这是算增设的喷头。和成排管道一样的道理。

徐海金 2023-02-13 15:34 00 [回复]举报

当然需要。你这是算增设的喷头。和成排管道一样的道理。

江抚陈工 2023-02-14 09:03 00 [回复]举报

 7.1.13 装设网格、栅板类通透性吊顶的场所,当通透面积占吊顶总面积的比例大于70%时,喷头应设置在吊顶上方,按照这执行;采用下喷市再吊顶下 应该设置挡水板;再吊顶内直立型喷头就可以,其他按照规范执行。

消防网友62117 2023-02-24 13:56 10 [回复]举报

关闭

关闭

手机APP下载