消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

连廊两端是否要加装防火门

1、高层住宅(32层),有人说在连廊与前室入口处可以不安装防火门。这样说,依据的是哪部法规的第几条啊?

2、也有人说依据《建筑设计防火规范》(2018版)第6.4.3.4条规范:疏散走道通向前室以及前室通向楼梯间的门应采用乙级防火门。需要安装防火门。

3、图中是开发商前期规划的,是有安装门的,但后期实际完成后没有防火门只有门套,麻烦请教下这里是不是必须要安装门,非常感谢

亮008 | 2023-08-01 04:27
请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


回答 | 5

同同不同 2023-08-01 08:06 00 [回复]举报

规范未明确是否必须要安装门或防火门;

走道通向前室、前室通向楼梯间您提供的图纸均为乙级门,满足相关要求;

但个人认为,按照建规图示6.6.4或室外楼梯应设置乙级门,另外参照室外疏散楼梯等相关要求,连廊或天桥距离其他门窗洞口距离不应小于2m,即与您图中南侧立面不小于2m。

二公子二公子 2023-08-01 09:39 00 [回复]举报

图纸设计,并且已经经过图审,建议最好是按图施工。

匠人营国 2023-08-02 08:02 10 [回复]举报

开敞外廊属于疏散走道,开在疏散走道上的室内与室外联通门不需要为防火门,如果气候许可也不需要必须安装。

陈曲 2023-08-02 10:43 00 [回复]举报

如果中间有分户墙,属于不同的防火单元,连廊两个门距离大于13米就可以不设置防火门

风无心 2023-08-04 18:34 00 [回复]举报

你可以自己判断,连廊是什么功能,图中明显就是疏散走道的功能,这门是可以不用装的,且对于疏散来说更有利,否则于从对面疏散过来的人来说,这道门装了以后是反向的。

关闭

关闭

手机APP下载