消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

自喷系统控制方式

为什么自喷系统,设置了报警阀压力开关直接连锁启动消防泵,还有另外设置压力开关信号和火灾报警信号两个信号与联动控制消防泵?

patrick | 2023-09-06 10:40
请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


回答 | 4

安洪全 2023-09-06 11:12 00 [回复]举报

需要火灾自动报警系统联动控制的消防设备,其联动触发信号应采用两个独立的报警触发装置报警信号的“与”逻辑组合。是保证自动消防设备(设施)的可靠启动的基本技术要求。


设置了报警阀压力开关直接连锁启动消防泵是因为其可靠性高,不冲突。


您可以理解为不同规范对同一系统的各自要求。“直接连锁启动消防泵”是自喷规范对本系统的最低要求,“联锁启泵”是火灾自动报警系统的基本要求。


阳明心   回复: 安洪全2023-09-07 09:09

“直接连锁启动消防泵”是自喷规范对本系统的最低要求,“联锁启泵”是火灾自动报警系统的基本要求。这两种需要同时具备的吗

0    0 [回复]举报

安洪全   回复: 阳明心2023-09-07 10:39

对,既能靠压力开关直接启泵,也能在形成“与”逻辑后联锁启泵,同时兼具这两种能力。

0    0 [回复]举报

陈曲 2023-09-06 17:10 00 [回复]举报

这个坏了咋整

关闭

关闭

手机APP下载