排烟风管包裹采用离心玻璃棉是否可行?

排烟风管包裹采用离心玻璃棉是否可行?

WeiHL | 2023-11-06 16:17
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 5

我的是昵称 2023-11-07 08:59 10 [回复]举报

不可行。离心玻璃棉的工作温度在200℃以下,适合用在低温管道。 而排烟管道防火要达到1.5小时,温度在达到280度时排烟风机停止工作,而管道肯定是超过280度的。

WeiHL   回复: 我的是昵称2023-11-09 16:08

谢谢大佬

1    0 [回复]举报

whale 2023-11-07 10:11 00 [回复]举报

防火包裹可以参考22K311-5,附录一

WeiHL   回复: whale2023-11-09 16:09

谢谢大佬

0    0 [回复]举报

潘天坤 2024-06-19 22:28 00 [回复]举报

市面上离心玻璃棉产品一般燃烧性能不符合规范要求

同时此做法无通风管道耐火极限报告,耐火极限可能不符合规范要求