消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

电缆层是否需增加消防报警设备

上级检查要求我们电缆隧道,地上电缆层要增加消防探测设备:如感烟

但实际我们电缆有感温探测器了,还需要另外增加感烟设备吗?

他参照的标准是建规8.4,但是我没有看到规范有说要增加

请专家帮忙解答一下

蒋林 | 2023-12-25 09:18
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 2

安洪全 2023-12-25 11:09 20 [回复]举报

检查的依据是建规的8.4.1中的第九项吗?如果是,已经被通用规范废止了。

而且,温感也是探测器的一种,并且这个温感的探测阶段可能还要早于烟感,因为有烟是已经烧起来了,温度变化会早于起火。


型式批准 2023-12-27 22:16 00 [回复]举报

电缆桥架只做感温电缆即可。

关闭

关闭

手机APP下载