消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

排烟窗间距

《建筑防烟排烟系统技术标准》GB 51251-2017 条文4.3.3中第5条是:设置在防火墙两侧的自然排烟窗(口)之间最近边缘的水平距离不应小于2.0m。可是专家说挡烟垂壁分开的两个防烟分区之间的排烟窗要单独设置且距离要大于2m,专家提的意见对不对?



酸奶不酸 | 2024-01-04 13:24
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 5

周家斌 2024-01-04 16:06 00 [回复]举报

挡烟垂壁处这样要求没有依据的,其实《建筑防烟排烟系统技术标准》GB 51251-2017 条文4.3.3中第5条的来源是《建规》要求,如下

酸奶不酸   回复: 周家斌2024-01-05 11:05

你这个是防火墙,我这建筑没有防火墙呀

0    0 [回复]举报

周家斌   回复: 酸奶不酸2024-01-06 10:05

所以不需要啊

0    0 [回复]举报

whale 2024-01-04 17:16 00 [回复]举报

没啥对不对,规范没规定

专家可能有自己的考量,这种问题需要和专家沟通了解下他提这条的想法。

酸奶不酸   回复: whale2024-01-05 11:09

有自己的考量也需要有规范依据吧,审不过设计师自己掏钱交二审审图费的,第一次提意见不提,故意不让过的,跟专家沟通了还分不清防火分区和防烟分区。

0    0 [回复]举报

关闭

关闭

手机APP下载