报警阀间和气体钢瓶间要不要设备用照明?根据哪条规范条文?

易学 | 2024-02-22 08:15
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 9

安洪全 2024-02-22 11:33 00 [回复]举报

需要

消防应急照明和疏散指示系统技术标准 GB51309-2018

3.8.1 避难间(层)及配电室、消防控制室、消防水泵房、自备发电机房等发生火灾时仍需工作、值守的区域应同时设置备用照明、疏散照明和疏散指示标志。

易学   回复: 安洪全2024-02-22 21:33

报警阀间着火也要工作或值守吗?

0    0 [回复]举报

安洪全   回复: 易学2024-02-23 12:51

不需要值守,但属于发生火灾时仍需工作的场所

0    0 [回复]举报

易学   回复: 安洪全2024-02-23 15:02

这里的工作是指报警阀设备在工作还是人在这工作?

0    0 [回复]举报

安洪全   回复: 易学2024-02-23 17:29

指报警阀设备在工作。


火灾发生时,如果系统启动不正常肯定要来设备间察看阀的工作状态,备用照明在这个时候就时有必要。

1    0 [回复]举报

易学   回复: 安洪全2024-02-26 10:31

这样理解就对了

0    0 [回复]举报

易学   回复: 安洪全2024-02-26 10:35

再请问下,这里的疏散照明是不是应急照明?

0    0 [回复]举报

安洪全   回复: 易学2024-02-26 12:04

疏散是疏散,应急是应急

疏散是指示方向用的,应急是照亮疏散通道的

1    0 [回复]举报

易学   回复: 安洪全2024-02-26 15:19

感谢感谢,学得透彻!