消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

氨压缩机厂房与氨火炬防火间距的问题请教

去年内蒙古消防总队检查出我单位氨压缩机厂房与氨火炬之间的16米防火间距不符合要求,现请教各位老师如何答复!

于立群 | 2024-05-10 20:45
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 6

消防网友68723 2024-05-11 12:02 00 [回复]举报

建规:乙类厂房与与明火或散发火花地点,不宜小于30m。

消防网友44826 2024-05-11 15:13 10 [回复]举报

首先氨制冷为乙类,火炬为明火或散发火法地点。按照《建筑设计防火规范》第3.4.1注:1 乙类厂房与重要公共建筑的防火间距不宜小于50m;与明火或散发火花地点,不宜小于30m。这个要求是已经被废止的,属于非强制条款。新的《建筑防火通用规范》GB 55037-2022第3.2.1 甲类厂房与人员密集场所的防火间距不应小于50m,与明火或散发火花地点的防火间距不应小于30m。仅对甲类厂房有要求。但考虑到氨的易燃易爆及毒性属性,建议对压缩机房或火炬采取安全措施(自行考虑)。

冰糖橙 2024-05-11 15:30 00 [回复]举报

建规要求乙类与明火不宜小于30米,但是通规把这条废止了。

胡胡203 2024-05-11 15:39 00 [回复]举报

氨压缩机房是乙类厂房与明火或散发火花的地点的防火间距参考:

建筑设计防火规范 GB50016-2014(2018年版)第3.4.1条 注:1 乙类厂房与重要公共建筑的防火间距不宜小于50m;与明火或散发火花地点,不小于30m。

虽然本条款是黑体强条,但30m用的是字条款,有回旋余地,如设计图纸上防火间距就是16米,且图纸是经过图审盖章的,建议参照图纸执行。

张冬华 2024-05-12 09:57 00 [回复]举报

化工规60米,50183是120米,都是可能有液体。没有液至少30米。你这明显不够啊

于立群   回复: 张冬华2024-06-03 12:23

按石化规的明火设备走的

0    0 [回复]举报

关闭

关闭

手机APP下载