消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

建筑设计防火规范 GB50016-2014(2018年版)第6.2.7条配电间设置甲级防火门不是强制条款,现在卡哪个规范哪一条?

建筑设计防火规范 GB50016-2014(2018年版)第6.2.7条配电间设置甲级防火门不是强制条款,现在卡哪个规范哪一条?

西西123456 | 2024-05-21 10:45
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 8

安洪全 2024-05-21 11:04 10 [回复]举报

建筑防火通用规范 GB55037-2022

6.4 防火门、防火窗、防火卷帘和防火玻璃墙


西西123456   回复: 安洪全2024-06-06 15:36

你好,强电间未设置防火门,不符合《建筑防火通用规范》(GB55037-2022) 第 6.4.4 条第 4 项之规定;卡这一条可以吗?

0    0 [回复]举报

周家斌 2024-05-21 15:18 10 [回复]举报

6.2.7条继续执行

消防网友68723 2024-05-21 16:22 10 [回复]举报

通规:4.1.4 燃油或燃气锅炉、可燃油油浸变压器、充有可燃油的高压电容器和多油开关、柴油发电机房等独立建造的设备用房与民用建筑贴邻时,应采用防火墙分隔,且不应贴邻建筑中人员密集的场所。上述设备用房附设在建筑内时,应符合下列规定:

    1 当位于人员密集的场所的上一层、下一层或贴邻时,应采取防止设备用房的爆炸作用危及上一层、下一层或相邻场所的措施;
    2 设备用房的疏散门应直通室外或安全出口;

    3 设备用房应采用耐火极限不低于2.00h的防火隔墙和耐火极限不低于1.50h的不燃性楼板与其他部位分隔,防火隔墙上的门、窗应为甲级防火门、窗。

一路同行 2024-05-21 16:28 10 [回复]举报

建规第6.2.7条是强条要求设甲级门;                                                                                                                通规第4.1.8条要求是防火门同时要求2小时隔墙,1.5小时楼板分隔;                                                                        个人认为应设甲级防火门


phone0224 2024-05-22 16:01 10 [回复]举报

6.2.7取消强制性也是应字条款啊,还是照样要执行的。

潘天坤 2024-06-16 16:47 00 [回复]举报

挺多人认为当被废止的条文与防火通用规范不存在冲突,可以暂时作为非强制性条文执行。

可以继续按照建规提出要求

xie00 2024-08-28 15:04 00 [回复]举报

《20kV及以下变电所设计规范》 GB50053-2013 >6.1.3(黑体强条)

关闭

关闭

手机APP下载