关于高大空间的气体灭火系统

对于高大空间的气体灭火系统,也要做到全室淹没吗?还是只需根据需求淹没建筑下部

zzyzy | 2024-06-03 09:43
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 2

黄辉 2024-06-04 08:31 00 [回复]举报

2.1.2 全淹没灭火系统 total flooding extinguishing system     在规定的时间内,向防护区喷放设计规定用量的灭火剂,并使其均匀地充满整个防护区的灭火系统。


从定义可知,需要整个防护区都充满灭火剂,不能只淹没下面。

气体灭火剂具有弥散性,喷出后会扩散至整个防护区,如果只要求淹没下部,会导致防护区灭火剂量减少,防护区达不到灭火浓度,导致灭火失败。

我头发贼黑 2024-06-04 09:17 00 [回复]举报

3.2.4 防护区划分应符合下列规定:     1 防护区宜以单个封闭空间划分;同一区间的吊顶层和地板下需同时保护时,可合为一个防护区;