消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

防烟机房、排烟机房内风管有耐火极限要求吗?

防烟机房、排烟机房内风管有耐火极限要求吗?

| 2024-06-05 18:45
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 2

同同不同 2024-06-06 08:28 00 [回复]举报

按照烟规应满足耐火极限

潘天坤 2024-06-06 08:42 10 [回复]举报

1、机房内:排烟机房内排烟管道耐火极限不应低于0.5小时(设备用房排烟管道耐火极限可不低于0.5小时);加压送风机房内未在吊顶区域的水平加压送风管道耐火极限不应低于1小时(水平设置的送风管道,当未设置在吊顶内时,其耐火极限不应低于1小时);加压送风机房内在吊顶区域的水平加压送风管道耐火极限不应低于0.5小时(水平设置的送风管道,当设置在吊顶内时,其耐火极限不应低于0.5小时)。

2、机房内风井连接处:排烟机房、加压送风机房内与风井连接处防火阀前后2米管道耐火极限不应低于1小时(风井耐火极限不低于1小时,穿越防火隔墙时应采用不低于隔墙耐火极限的保护措施)。

3、地下室穿越机房隔墙处:地下室排烟机房、加压送风机房穿越机房处防火阀前后2米排烟管道耐火极限不应低于2小时(排烟机房隔墙耐火极限不低于2小时,穿越防火隔墙时应采用不低于隔墙耐火极限的保护措施)。



关闭

关闭

手机APP下载