消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

核心筒结构办公楼,客梯厅两侧通道安装门禁是否合规

您好,请问一下核心筒结构办公建筑,客梯与消防梯独立,整层使用用户为了安全控制外来人员,计划将客梯厅两侧装玻璃门及门禁,这样可能导致紧急情况电梯厅的人疏散不出去,应该不符合规范,详细如图,请各位老师帮解答,是否符合要求,谢谢!

南飞野雁 | 2024-06-10 10:47
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 5

黄-江西省景德镇市 2024-06-11 00:08 00 [回复]举报

1、火灾发生时,所有门禁可通过火灾报警联动释放;(门禁系统具备此联动功能或门禁系统的电源被强切断电后具备自动释放功能,可以实现)

2、门的开口宽度需要满足紧急情况下三部电梯满载人员数的疏散要求;

3、门的开口高度建议平吊顶或无吊顶的结构梁,以免门楣起到挡烟作用,使得烟气在侯梯厅内聚集影响疏散;

4、侯梯厅两侧隔断玻璃(含门)的耐火极限不低于1.0h。

须尽欢 2024-06-11 09:26 00 [回复]举报

安装玻璃门可以,门禁需要做联动控制系统,联动情况下切断电源让门禁断电

李良敏 2024-06-11 10:01 10 [回复]举报

用门禁系统不是问题,规范并没有禁止,火灾报警联动时可以打开就行。有问题的是:

1.多半采用耐火极限不达标的玻璃隔断和玻璃门;

2.很多采用的是平移式自动感应门,不符合平开门要求。

一个呆呀 2024-06-11 10:01 10 [回复]举报

这种事常见,基本上都会切非开门,关键是宽度和防火玻璃基本上不达标

潘天坤 2024-06-16 10:17 10 [回复]举报

楼上几位老师说的挺全面的。

设置门禁,当确认火灾应具有打开疏散通道上由门禁系统控制的门的功能。

疏散走道墙体有1小时耐火极限要求,市面上玻璃隔墙材料一般无法满足相关要求。

同时要满足疏散宽度要求和疏散门的平开门要求。


关闭

关闭

手机APP下载