消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

分区供水的理解

现有一150米公共建筑,在80米处分区供水。高区有消防水箱和稳压泵,那现在的室内消火栓最不利点静压值是整体>0.15兆帕呢,还是分别高区>0.15,低区≥0.1呢

哇咔 | 2024-07-19 17:23
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0

回答 | 5

安洪全 2024-07-22 08:37 00 [回复]举报

消防给水及消火栓系统技术规范 GB50974-2014

5.3.3 稳压泵的设计压力应符合下列要求:     

1 稳压泵的设计压力应满足系统自动启动和管网充满水的要求;    

2 稳压泵的设计压力应保持系统自动启泵压力设置点处的压力在准工作状态时大于系统设置自动启泵压力值,且增加值宜为0.07MPa~0.10MPa;    

3 稳压泵的设计压力应保持系统最不利点处水灭火设施在准工作状态时的静水压力应大于0.15MPa。

哇咔   回复: 安洪全2024-07-22 11:39

这个条文,我都背下来了。才问的这个高低分区

0    0 [回复]举报

安洪全   回复: 哇咔2024-07-22 12:43

无论高区、低区,设稳压泵都是0.15

0    0 [回复]举报

安静等待 2024-07-22 09:30 10 [回复]举报

有一种情况是高区、低区各自分开补水。当高区用稳压装置补水,最不利点压力≥0.15Mpa,低区单独从屋面水箱接补水管并采取减压措施给低区补水,此时低区最不利点压力是≥0.1Mpa。

哇咔   回复: 安静等待2024-07-22 11:38

不是≥0.15,是>0.15

0    0 [回复]举报

关闭

关闭

手机APP下载