哪些部位应设置出口标志灯?有相关规范条文吗?

哪些部位应设置出口标志灯?有相关规范条文吗?

峰峰 | 2024-07-30 11:03
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 1

消防资源网 2024-07-30 13:37 00 [回复]举报

消防应急照明和疏散指示系统技术标准 GB51309-2018


3.2.8 出口标志灯的设置应符合下列规定:
    1 应设置在敞开楼梯间、封闭楼梯间、防烟楼梯间、防烟楼梯间前室入口的上方;
    2 地下或半地下建筑(室)与地上建筑共用楼梯间时,应设置在地下或半地下楼梯通向地面层疏散门的上方;
    3 应设置在室外疏散楼梯出口的上方;
    4 应设置在直通室外疏散门的上方;
    5 在首层采用扩大的封闭楼梯间或防烟楼梯间时,应设置在通向楼梯间疏散门的上方;
    6 应设置在直通上人屋面、平台、天桥、连廊出口的上方;
    7 地下或半地下建筑(室)采用直通室外的竖向梯疏散时,应设置在竖向梯开口的上方;
    8 需要借用相邻防火分区疏散的防火分区中,应设置在通向被借用防火分区甲级防火门的上方;
    9 应设置在步行街两侧商铺通向步行街疏散门的上方;
    10 应设置在避难层、避难间、避难走道防烟前室、避难走道入口的上方;
    11 应设置在观众厅、展览厅、多功能厅和建筑面积大于400m²的营业厅、餐厅、演播厅等人员密集场所疏散门的上方。