多孔板吊顶算不算格栅吊顶

一种多孔板吊顶(孔很小),通透率约19.6%,算不算格栅吊顶?因为关系到此处的喷淋设置和防排烟设置,很重要。

忙里偷闲 | 2024-08-14 09:57
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 5

消防网友70474 2024-08-14 12:27 00 [回复]举报

只看镂空率,不用看格栅是哪种类型

LHH2737 2024-08-14 14:03 20 [回复]举报

算,但是你这个通透率太小了,直接按密封性吊顶考虑就行

自喷规范 7.1.13 装设网格、栅板类通透性吊顶的场所,当通透面积占吊顶总面积的比例大于70%时,喷头应设置在吊顶上方,并应符合下列规定:

1 通透性吊顶开口部位的净宽度不应小于10mm,且开口部位的厚度不应大于开口的最小宽度;

2 喷头间距及溅水盘与吊顶上表面的距离应符合表7.1.13的规定。

防排烟规范 4.2.2 对于有吊顶的空间,当吊顶开孔不均匀或开孔率小于或等于25%时,吊顶内空间高度不得计入储烟仓厚度。

4.4.13 当排烟口设在吊顶内且通过吊顶上部空间进行排烟时,应符合下列规定:非封闭式吊顶的开孔率不应小于吊顶净面积的25%,且孔洞应均匀布置。

消防网友5724 2024-08-14 17:49 00 [回复]举报

通透率太低了,按照封闭吊顶考虑

阿宸宸宸宸OK 2024-08-14 23:10 00 [回复]举报

不属于格栅吊顶,镂空面积也达不到啊

潘天坤 2024-09-12 14:34 00 [回复]举报

有开孔的吊顶就属于通透性吊顶,通透性吊顶需要考虑通透率(开孔率),同时要注意开孔均匀分布


按照楼主描述这种通透性吊顶的通透率(开孔率)为19.6%,从暖通专业来说:通透率(开孔率)未大于25%约等于密闭式吊顶,吊顶内空间高度不计入储烟仓厚度,空间净高为吊顶距地高度

从给排水专业来说:通透率(开孔率)未大于70%,喷头可不设置在吊顶上方(当然净空高度大于0.8米的闷顶和技术夹层内如果存在可燃物,应设置洒水喷头)