石油库储罐区的室外消火栓,采用临时高压供水系统。那么,室外消火栓的出水压力要求达到多少满足要求?

请教一下:石油库储罐区的室外消火栓,采用临时高压供水系统。那么,室外消火栓的出水压力要求达到多少满足要求?

alin绿萝 | 2024-08-31 18:20
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 2

张治福 2024-09-02 10:53 00 [回复]举报

先需要说明的是:室外消火栓的主要功能是为消防车提供水源的。

另《石油库设计规范》已有明确要求了。你所提及的临时高压供水系统,按照高压消防给水系统设计。

12.2.3 当石油库采用高压消防给水系统时,给水压力不应小于在达到设计消防水量时最不利点灭火所需要的压力;当石油库采用低压消防给水系统时,应保证每个消火栓出口处在达到设计消防水量时,给水压力不应小于0.15MPa。


另从你的表述中,推测是消防冷却水系统设置的移动式消火栓,那么,它的出水压力就要取决于储罐高度、水枪喷嘴处所要求的压力及水带压力损失综合确定的。


拙见,仅供参考。

alin绿萝   回复: 张治福2024-09-06 11:45

首先表示感谢。前辈的表述和逻辑很清晰。现场是固定消火栓。

0    0 [回复]举报