消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

消防检测报告

对现场消防设施未进行全数测试,只是抽检并进行联动测试就出具合格的检测报告,是否属于出具虚假报告?

消防打工人 | 2021-07-02 00:03
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 4

yizhongdayang 2021-07-02 09:55 00 [回复]举报

       所谓虚假报告,是指未提供消防技术服务或者以篡改结果的方式出具的报告;或者与出具与当时实际情况严重不符、结论定性严重偏离客观实际的报告。

       按各地消防设施检测技术规程要求,并不是所有的消防系统都要做全数测试,比如火灾探测器的抽检比例为10%-20%,防火卷帘抽检比例为不少于25%等等,而消防水泵、湿式报警阀、防排烟风机等都要求全数测试(以上要求摘自辽宁省地标)。所以按照所在省市的消防检测地方标准要求进行检测,是符合要求的,不属于虚假报告。


消防打工人   回复: yizhongdayang2021-09-09 23:29

不全检怎么能保证与实际情况相符?现场有太多不注册、不开号的情况,不全检就发现不了。

0    0 [回复]举报

阳明心   回复: 消防打工人2023-04-10 14:45

按规范要求来,如果全测,要配备多少消防检测人员啊,要多少钱啊,得考虑实际效益,对量大的点位应该抽检,而不是全检。

0    0 [回复]举报

消防打工人   回复: 阳明心2023-07-29 20:49

不一定要一个一个用烟枪试才能发现问题,现实是检测时没人核对现场设备实际安装数量与控制器连接数量是否有差异。在主机上查一下设备数量再与竣工资料里的设备数量比较一下也增加不了多少人工成本吧?不想做的事总能找到借口!

0    0 [回复]举报

关闭

关闭

手机APP下载